What's the second image you posted?
bore holes to the mine
900'
the sec cables are lowered down them and suspended by wire rope
500 mcm
Thanks. What type of mine is it and what equipment is the new substation running?
Small job, wasn't it?
:lol:
Never seen a built in test panel. How does the variac test current elements? Or is that just for the UVs and such?ngr gf and potential protection section
also variac for weekly testing of
each cb oc, toc, gf/0 seq, uv drop out
ngr i and v
ground wire monitors
Awesome
Why strung bus and not AL tube? Id imagine bus work would be a clearance issue?
cost
Never seen a built in test panel. How does the variac test current elements? Or is that just for the UVs and such?
Ahhh :thumbsup: How much % wise?
How long did it take to commission? What's standard protocol on commissioning new equipment such as the pictures of the substation?