Nope, that is the same as the OP is asking.Wat about a mineralac strap on a pvc conduit from meter base that a GEC runs in to ground rod ?
Roger
Nope, that is the same as the OP is asking.Wat about a mineralac strap on a pvc conduit from meter base that a GEC runs in to ground rod ?
Sure it's a raceway, it's just a short one.250.64(E) mentions raceways and enclosures I don't see this strap as being either.
I agree, but also feel the same way about something like a chase or close nipple encircling the GEC. I can almost guarantee most inspectors will ignore any possible choke effect of a strap but will reject a chase or close nipple if it isn't bonded on both ends, and some will even act like it may be the worst thing they have ever seen:roll:Just my 2 cents, a 1" piece of metal encircling the GEC and having any real detrimental effect is absurd.