Mini split A/C systems

Status
Not open for further replies.

Leespark57

Senior Member
Location
Boston, MA, USA
I'm assuming the cable you are referring to is tray cable. See 336.10(9). Tray cable type ER (exposed run) JP (joist pull), in one and two family dwellings follows Part II of 334 (non-metallic sheathed cable).
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Greg it would be helpful if you actually asked a question. If you are talking about the rubber cord than that cannot run thru walls.
 