kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
My thoughts on this are you don't need a disconnect at the air handler anyway unless it is rated over 1/8 hp or 300VA. It has no hermetic compressor so 440 doesn't apply to it.If you are required to have a disconnect switch at the air handler, a basic 2 pole wall switch is all you need. You do not need a 3 pole switch. The control line is low voltage and may even be optically coupled further reducing any shock hazard.
Never seen a minisplit with large enough motor/VA rating that would kick in that requirement. If there is one out there, they might want to rethink that "mini" in the name.:happyyes: