Mini split

Status
Not open for further replies.

Tcouillard

Member
Location
New Hampshire
Occupation
Electrician
Need help figuring out what size wire and breaker I need for a mini split it says minimum breaker size is 20 and max 25. So not sure if I should do 10 gage wire on a 30 amp breaker. Also if someone could reference a code article that would be great think I’m just looking in the wrong area
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
It should say M(inimum) C(ircuit) A(mpacity) and M(aximum) O(vercurrent) P(rotection).

Size the wire by the former (#12) and the breaker by the latter (25a).
 

Tcouillard

Member
Location
New Hampshire
Occupation
Electrician
Use a 25 amp breaker. A 20 May nuisance trip. The nameplate should tell you the minimum circuit ampacity. For example if it shows 19.9 amps MCA you could use #14 thhn or #12 nm cable.
But if use a 25 amp breaker should I use #10nm since 12 is only rated for 20amps
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
True actually but can only be protected by 20amps unless on a motor load is that why I could get away with that?
Yes. Load has its own overload protection so your breaker only provides short-circuit protection.

The allowance is to permit short-term starting current.
 