Note that I said "code issues aside".
Yeah am totaly with ya, I was playing UL product evaluation engineer up there.

Since they are UL listed units someone has gone thru the calcs and decided its safe.
I find it fascinating that part of a branch circuit that goes in walls is designed by a UL product listing.
It would be like a light and a switch being sold together and the instructions saying I can install the light on a 20A circuit and run 14AWG for a switch loop.
Whomever was the designer used the NEC, and I would like to retrace their logic.
The point is that it is done in the field daily and while technically a violation, it is not that unsafe IMO.
I agree we install them often. As Kwired said the most common installs are a 15 or 20 which then there is no issue in my mind.
I don't know that its a violation to use the tray cable, that line hide stuff is the "tray". I just observed a single Daikin 30A outdoor units design has no additional protection for the 14AWG leading me to call it a tap. Other brands may have internal protection. I would be really interested to see what others find on 30A units. Do other brands have internal overloads or OCPD for the indoor unit feed?
The indoor fan is not going to pull more than a few amps. And if there is a short, a 30a breaker will still trip with 14awg attached and no damage to the wire.
I hope so. They are UL listed so electrical contractors liability ends with following the instructions. It seems there is a class 2 power supply and a lot of electronics in them as well. if I was conducting forensic electrical fire investigation and traced a house fire to a indoor unit I would be very interested as to what kind of OCPD it was ultimately protected by.
It's a closed system and that's why some inspectors may overlook the issue altogether.
I expect the NEC will look at this sooner or later. Too many question here and on other forums regarding minisplits. Classic split systems are pretty clear as to OCPD requirements on each end but minisplits have this unique wiring scheme for the indoor unit.
Yes and I imagine we did not cover all the possible ways it may be allowed. For example it could be argued that the 14AWG "tap" does not even meet the definition of
branch circuit and is part of the appliance.
The overcurrent protective device for the unit is there only for short circuit and ground fault, the unit itself has overload protection built in which will protect the wire. The load at the unit still cannot be more than 15 amps for a 14 gauge if you use nm cable. If the 14 wires is rated 75C then you can use the wire at the 20 amp capacity. The overcurrent protective device, however, can be higher
Yes I agree Dennis, however most respectfully do you agree the maximum rating of the inverse time breaker (regular residential plug in HACR breaker) should be determined by using Table 430.52?
We all seem to agree that the indoor blower is an
applianceand the "tap" conductors does not need the switch so hopefully that helps others.