Saturn_Europa
Senior Member
- Location
- Fishing Industry
- Occupation
- Electrician Limited License NC, QMED Electrician
My organization works in countries primarily on the 400/230 50 hz standard.  We use 2 pole miniature circuit breakers with a B curve.  The B curve will trip the magnet part of the thermal magnet breaker in 3 to 5 times the current rating.  C curves will trip at 5 to 10 times the current rating. We use B curve because we are often on  generator power and 10 times the current rating of a 63 amp breaker will be a larger fault current then the genset can provide and cause a fire.  Below is a link to a common breaker we use.  
	
	
		
			
			
				
					
						
							 www.se.com
						
					
					www.se.com
				
			
		
	
We are setting up a project in Haiti on the US standard. Most of the electrical equipment in Haiti is residential US brands sent from Florida.
What is the trip curve of a Square D QO, 20A, 1 pole, 120/240VAC? I cant find much on trip curves for NEMA rated equipment.
I found this document but do not understand it:
	
	
		
			
			
				
					
						
							 www.se.com
						
					
					www.se.com
				
			
		
	
In fact I had never heard of a B or C curve breaker until I started working over seas. Are off the shelf Homeline, QO, GE, Siemens, or Eaton residential breakers given a trip curve such as B, C, D, K and Z curves like MCBs are?
Any help would be appreciated.
	
		
			
		
		
	
				
			A9F76225 - Miniature circuit-breaker, Acti9 iC60N, 2P, 25 A, B curve, 6000 A (IEC 60898-1), 10 kA (IEC 60947-2) | Schneider Electric Egypt
Schneider Electric Egypt. A9F76225 - Miniature circuit-breaker, Acti9 iC60N, 2P, 25 A, B curve, 6000 A (IEC 60898-1), 10 kA (IEC 60947-2).
				We are setting up a project in Haiti on the US standard. Most of the electrical equipment in Haiti is residential US brands sent from Florida.
What is the trip curve of a Square D QO, 20A, 1 pole, 120/240VAC? I cant find much on trip curves for NEMA rated equipment.
I found this document but do not understand it:
Trip Curve: QO 20A 1P - No. 730-03 | Schneider Electric
Trip Curve: QO 20A 1P - No. 730-03
				In fact I had never heard of a B or C curve breaker until I started working over seas. Are off the shelf Homeline, QO, GE, Siemens, or Eaton residential breakers given a trip curve such as B, C, D, K and Z curves like MCBs are?
Any help would be appreciated.
 
				
 
 
		 
 
		 
 
		 
 
		