This forum is, in general, specific to the US National Electric Code. Your task would likely require knowledge of the governing codes in the region where the installation is.
If you are using IEC MCBs, they come with different "trip curves" having mostly to do with their Instantaneous trip current characteristics. Generally, most manufacturers use what are referred to as "A, B, C, D" trip curves, whith D being the one designed for use on transformer primaries.
But your inclusion of the fact that you have an 11kV incomer is what bothered me. MCBs are generally NOT considered for use where there is a high available fault current, such as would likely be the case if you are coming right off of an 11kV transformer primary. MCBs are not typically capable of more than 10kAIC. You would want to use an MCCB because they typically have Interrupting Capacities of 30KA and above. However this is where your local code rules will come into play as well. You could NEVER do this in the US, but you may be able to in some other country with looser rules.
The question is a bit ambiguous.
Miniature circuit breakers?
MCB (Miniature Circuit Breaker)?rated current not more than 100 A. Trip characteristics are not normally adjustable. Thermal or thermal-magnetic operation.
Miniature Branch Circuit Protection
or
Miniature Supplemental Protection
Which is it, branch circuit protection of supplemental protection?
The NEC addresses supplementary protectors in that they are not for use for branch circuit protection.
A branch circuit protective device is UL489 where the supplemental protective device is a UL1077 device.
You must provide branch circuit protection first and foremost and then can put UL1077 supplementary protective devices anywhere you heart desires.
Jraef,
...
Again, supplementary protectors are UL1077 devices.
I would like to emphasize that this IEC breaker is recognized by UL under UL 1077.
The UL1077 devices are used where branch protection is required (for example UL 489 MCCB) that is already provided or not required.
Regardless of where you are and what codes may apply if always makes since to provide branch circuit protection first and then use supplemental protectors where it may sense to provide additional coordination.