mjc1060

Senior Member
Hi, I am installing a 400A 480V panelboard and I was instructed to match existing heights. My question is does the NEC have a maximum height for a panelboard main disconnecting circuit breaker and are there any requirements (such as height) for the cabinet that contains the the panelboard?
:?
 
404.8 provides for the maximum height of the switch (breaker) (6'7"). I know of no requirement for the panelbaord height itself.
 