Is it true that even with a 480 3PH / 1 HP motor / 2.1Amps I can only use a 15A CB and not smaller?
 
No.

It is true that you are not required to use less than a 15A CB though.

Where is this in the code covering this?
It is also permissible for me to use 14AWG for the motor? Seems somewhere there was a statement about 12AWG as minimum size for motor conductor.
 
Where is this in the code covering this?
It is also permissible for me to use 14AWG for the motor? Seems somewhere there was a statement about 12AWG as minimum size for motor conductor.

There is no code requirement for #12 as a minimum. It is a common industrial spec though. Purportedly because #12 is less likely to be damaged when pulled.

Take a look at 240.4 (B) and T240.6(A).
 