K kuchenig Member Apr 26, 2004 #1 Section 300.5 on Underground Installations seems to be aplicable to all cable voltage levels but Table 300.5 provides minimum cover requirements for cables 0 to 600 volts only. Where are cables over 600 volts tabularized or discussed? Thanks
Section 300.5 on Underground Installations seems to be aplicable to all cable voltage levels but Table 300.5 provides minimum cover requirements for cables 0 to 600 volts only. Where are cables over 600 volts tabularized or discussed? Thanks
B bphgravity Senior Member Location Florida Apr 26, 2004 #2 Re: Minimum Cover of UG cables Over 600 Volts Article 300.50 for over 600 Volts, Nominal.
charlie Senior Member Location Indianapolis Apr 27, 2004 #4 Re: Minimum Cover of UG cables Over 600 Volts Ownership of the cables matters. If they are owned by the serving electric utility, different rules are applied.
Re: Minimum Cover of UG cables Over 600 Volts Ownership of the cables matters. If they are owned by the serving electric utility, different rules are applied.