Minimum Cover Requirement for Fiber Optic Cable

Status
Not open for further replies.

emccoy

New User
Location
Charlotte
Occupation
Electrical General Supt
I am trying to determine if there is a minimum cover requirement for 2" PVC40 containing nonconductive fiber optic cable. It does not seem to be addressed in 770 and it is unclear if 300-5 applies. Any help would be appreciated.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
And it’s best to be at 24” cover as that is the depth it’s expected be at. Otherwise the fiber optic locator (backhoe) will find it.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
And it’s best to be at 24” cover as that is the depth it’s expected be at. Otherwise the fiber optic locator (backhoe) will find it.
I think you are lucky in a lot of cases if they bury it all all. Sometimes they seem to just hide it in the grass like the cable installers do. :)
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Often fiber optic is installed by a telecom utility and if on the utility side of the demark it’s not regulated by the NEC.
 
Status
Not open for further replies.