I have specs for a RTU and I am confused how this DSS value was calculated and what it means... The unit is 3ph 460V and I am given this information:
Condenser Motor FLA= 2.2 A
4x condenser motors
Compressor 1 RLA= 20.5 A
Compressor 2 RLA= 31.7 A
Compressor 3 RLA= 31.7 A
Supply Fan FLA= 24.7 A
CCH FLA= 1.0 A
MCA= 127.0 A
MOP= 150.0 A
DSS= 250.0 A
I am not given the horsepower ratings of any of this, nor the locked rotor current or locked rotor code letters. The equivalent FLA of the unit comes out to 118.4 A, which when cross-referenced with NEC T430.250 gives equivalent HP of 100HP. The 200A HD disconnect I want to use is rated for 125HP at 480V. Does anyone know where this 250A DSS is coming from or what is the significance of this number? I feel like the 125HP rating of the 200A disconnect is adequate- am I wrong?
Condenser Motor FLA= 2.2 A
4x condenser motors
Compressor 1 RLA= 20.5 A
Compressor 2 RLA= 31.7 A
Compressor 3 RLA= 31.7 A
Supply Fan FLA= 24.7 A
CCH FLA= 1.0 A
MCA= 127.0 A
MOP= 150.0 A
DSS= 250.0 A
I am not given the horsepower ratings of any of this, nor the locked rotor current or locked rotor code letters. The equivalent FLA of the unit comes out to 118.4 A, which when cross-referenced with NEC T430.250 gives equivalent HP of 100HP. The 200A HD disconnect I want to use is rated for 125HP at 480V. Does anyone know where this 250A DSS is coming from or what is the significance of this number? I feel like the 125HP rating of the 200A disconnect is adequate- am I wrong?