Per UL 98, the standard that the horsepower rated disconnect is listed to, the disconnect capable of being opened under locked rotor conditions.
For switches rated 100 hp or less it must be able to do that 50 times without damage. For switches over 100 hp, it must be able to do that 10 times without damage.
The current used for this testing for a disconnect rated at 150 hp is 2170 amps at 240 volts, and 1085 amps at 480 volts.
Give the code full load currents of 360 amps and 180 amps for a 150 hp motor at 230 and 460 volts, the UL test currents equals the rule of thumb locked rotor current of six times full load.
Thats great info, Don. Thank you! I'll try to post a better reply with code references, but in looking at several examples....
LRA of compressors tends to be much higher than 6 times FLA. I bet thats the answer.... if I only can get that LRA data of the compressors, I bet it is over 150 HP equivalent and then this starts to make some sense.