wcv111

New member
I thought I saw somewhere once that a raceway cannot contain just one conductor. Is this true? If so, where in the NEC does this rule reside.

Thanks for your time :smile: .

Bill V.
Hartville, Ohio
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Nearly true. Most often true. Well, actually, there is no rule that says that, but it is a consequence of a rule.

300.3(B) tells us that all conductors of a given circuit must be in the same raceway. Since you can?t build a circuit with a single conductor, then you wind up having to have at least two conductors in a raceway. There are rare exceptions, called ?iso-phase? runs, but I do mean ?rare.?

 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Regardless of whether it was a code rule or not, the issues of EMF, EMI, and or Inductive heating would be reasons not to.

Roger
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
I recall reading about a WWII era wiring system used in Europe where the conduit itself was used as the grounded _conductor_. Single ungrounded wire in the conduit, devices connected between that wire and the conduit. Hope they carefully tightened up the connector screws :)

-Jon
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
What if I had two PVC boxes with two 1/2" PVC raceways between the two boxes? Couldn't I put one conductor in one raceway and two in the other?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
infinity said:
What if I had two PVC boxes with two 1/2" PVC raceways between the two boxes? Couldn't I put one conductor in one raceway and two in the other?
i s'pose so, but if they were that large, I'd prefer a single 3/4" conduit.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Dennis Alwon said:
Man, I bet Bill V. from Ohio wishes he never asked his question. lol Confused now???
OK. Let's give him a simple and truthful answer to the question that he asked. That would be a novel thing for us. :D

The answer is "No." There is no NEC rule that explicitly states that a conduit is not permited to contain only one conductor.
 

tryinghard

Senior Member
Location
California
?Hysteresis? might play a role?

?Hysteresis? might play a role?

Notice 300-20 & (B)(1) along with FPN

From my limited understanding: due to AC & its cycles the electromagnetic field of a single conductor causes the molecules in metal to align & re-align. This aligning & re-aligning causes induced heating know as ?hysteresis heating?.

With this considered it is best practice to avoid single conductors in conduit, especially metal. I think parallel conductors in single conduits [a most common application] act as a single conductor, and hysteresis needs to be considered.
 

Rockyd

Senior Member
Location
Nevada
Occupation
Retired after 40 years as an electrician.
Tryinghard got one part that is in referenced in the code. I'll throw in part two for discussion, believe that it covers the requirements of a single conductor in a conduit, or raceway...

Chapter 9 Table 1, Percent ofcross section of conduit and Tubing for conductors -

1 conductor - 53 % fill

2 conductor - 31 % fill

over 2 is the normal 40% fill note.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
tryinghard said:
Also notice 300-3 (B): ?All conductors of the same circuit?shall be contained within the same raceway?


You need to read down a little further. 300.3(B)(3) Nonferrous wiring methods are allowed to be in separate raceways.
 

tryinghard

Senior Member
Location
California
infinity said:
You need to read down a little further. 300.3(B)(3) Nonferrous wiring methods are allowed to be in separate raceways.

It appears the intent of this section is to control or eliminate induced heat and for single conductors: "shall comply with the provisions of 300-20 (B)" which I listed in post #11 above. The rest of this section seems to be for cable but again it is to control or eliminate induced heat.

I think the most common situation with single conductors causing hysteresis or induced heat is with parallels. Parallels in individual conduits or raceways act as one conductor with cycles.

Other that parallels one should simply avoid installing individual conductors of a circuit in separate conduits or raceways, this practice most often cannot comply with NEC.
 