minimum panelboard mains rating

Status
Not open for further replies.

123

Member
Location
New Jersey
are there panelboards made with mains rating of less than 100 amps?

i had to survey some old panelboards and could not identify the rating label, and many of them had 30 thru 70A MCBs. is it safe to assume that the mains are 100A?
 
In the first three pages of the Square D catalog I have at my desk, I see panelboards with mains rated at 30, 40, 60, and 70 amps. So no, it would not be safe to assume that the rating of any given panel is at least 100 amps.

Welcome to the forum.
 
Thanks for your reply, Charlie.

Would it be possible to see a link to this in an online catalog?

I took a loot at the Scheider Electric (Square D) and don't see anything less than 100A.

(sample attached)
 