bth0mas20 said:Thanks for all of your responses.
The install that ive decided on:
Single 30a circuit out of the house panel. Then 60ft of 10-2 uf underground to the detached garage. Up the side of the garage sleeved in pvc thru the wall to a 4 space panel (only 120v no 240v). No grounding electrode. One circuit fed by a 15a arc fault bkr for 4 medium base lights total. Then a 20a breaker to a GFCI protected outlet circuit with 4 outlets.
I probally put more info than was needed to explain this. I feel that this will be sufficient to pass code.
bth0mas20 said:I only plan to install 2 bkrs in the panel. Less than 6 throws. Why would I need a ground rod or two.
bth0mas20 said:I only plan to install 2 bkrs in the panel. Less than 6 throws. Why would I need a ground rod or two.
iwire said:You need a grounding electrode system because you are running a feeder there.
250.32(A)
And as far as the 'less then 3 throws of the hand' bit, it is really tough to accomplish legally in a detached structure, better off using a main breaker panel.
bth0mas20 said:I only plan to install 2 bkrs in the panel. Less than 6 throws. Why would I need a ground rod or two.
bth0mas20 said:I only plan to install 2 bkrs in the panel. Less than 6 throws. Why would I need a ground rod or two.
My bad, you're right. 100a would require a 1" PVC run; the 3/4" would be good for up to 60a.roger3829 said:Not sure about 3/4" being good for 100a.
How did you calculate that?
I get about 50a:-?
frizbeedog said:Just to be clear. A Grounding electrode is not required for a single circuit. See the exception to 250.32. This inculudes a MWBC.
Also see Art 225 Outside branch circuits and feeders
Edit....Had I continued to read the thread I would have known they already said that.
bth0mas20 said:I can run a 12/3 uf to a wp 30a disc outside then to the two seperate circuits. One for lighting and one for outlets right.
Because you now have a feeder serving the building and not a branch circuit. The grounding electrode exception only applies when the second building is served by a branch circuit.bth0mas20 said:I only plan to install 2 bkrs in the panel. Less than 6 throws. Why would I need a ground rod or two.
The way I look at it is pretty much if you put a panel board in the separate structure or run more than one circuit to it, it needs a GES.don_resqcapt19 said:Because you now have a feeder serving the building and not a branch circuit. The grounding electrode exception only applies when the second building is served by a branch circuit.
tryinghard said:Yep and so did I (ahead of "they") in Post #15, but thanks for your attention to this topic![]()
bth0mas20 said:Thanks for your comment. You really set me straight on that one.
I was just making sure because I just wasnt 100% sure of what was right. Sorry If it bothered you.