Okay, this scenario. A fixed pier with 34 slips and 34 boat lifts. Each lift has (2) 3/4HP motors. No other loads.
Since (2) motors start/stop as one I think you should count each slip at (2*6.9A @230V) 13.8A.
So, 1@1.25% is (13.8*1.25) 17.25A plus (33*13.8)455.4 = 472.65A calculated load.
Well there is no way in the world all of those lifts will operate at the same time. A 500-amp service IS NOT NEEDED for this to safely operate.
What is the minimum service required for this using the NEC?