I think Charlie may have the answer.
Bob I couldn;t think of a real life situation but let's look at a dryer. The neutral conductor is used for a motor that is rated under 20 amps at 120V. The dryer calls for 240V 30 amps so the egc is #10. I was told that the neutral could be sized for the 20 amps. I didn't believe it could be but that was my question--
There is also section 210.19(A)(3) that allows the neutral to be smaller than the range, wall oven, etc but never smaller than #10 which would be the EGC size for a 60 amp circuit.
Thanks again Charlie-- I believe that clears it up.
Bob I couldn;t think of a real life situation but let's look at a dryer. The neutral conductor is used for a motor that is rated under 20 amps at 120V. The dryer calls for 240V 30 amps so the egc is #10. I was told that the neutral could be sized for the 20 amps. I didn't believe it could be but that was my question--
There is also section 210.19(A)(3) that allows the neutral to be smaller than the range, wall oven, etc but never smaller than #10 which would be the EGC size for a 60 amp circuit.
Thanks again Charlie-- I believe that clears it up.