I am working on a job with a lighting control system. All of the outputs form modules to landscape lighting (some transformers, some direct loads) have been run through GFCI feed-thru devices rated 120VAC. All outputs were on dimmers (these are slowly being changed to relays unless they want to dim them). Does anyone know if the GFCI has a minimum voltage it must see?
There are multiple manufacturers, none with indicator lights, we are changing out the ones that seem to be nuisance tripping with COOPER VGFD20. We have found that MOST were actually tripping due to faults in the field, it is just cheaper to replace first. One stopped tripping when we moved the load to a relay output versus a dimmer output. Several are form water filled in-ground transformers - poorly installed I might add.
There are multiple manufacturers, none with indicator lights, we are changing out the ones that seem to be nuisance tripping with COOPER VGFD20. We have found that MOST were actually tripping due to faults in the field, it is just cheaper to replace first. One stopped tripping when we moved the load to a relay output versus a dimmer output. Several are form water filled in-ground transformers - poorly installed I might add.