minimum wire size for subpanel

Status
Not open for further replies.

difowler1

Senior Member
I thought I had read where the minimum size ungrounded conductor that could be used for subpanel feeder was #6. I cant find that in the 2020 nec at the moment.
 

difowler1

Senior Member
How about 225.39b. It sounds like its saying that the subpanel must be rated for at least 30amps if there will be 2 branch circuits. Therefore the feeders could be #10?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
How about 225.39b. It sounds like its saying that the subpanel must be rated for at least 30amps if there will be 2 branch circuits. Therefore the feeders could be #10?
Realize that Article 225 covers a sub-panel in a remote structure.
 
Status
Not open for further replies.
Top