I am going to run 30 amps out to a well house. Can I just run #10 to the ground rods or is there a minimum size allowed?
Nothing says this conductor has to be bare, and nothing states a specific insulation color for grounding electrode conductors, though many inspectors for some reason think they need to be green.Are you installing a sub panel? If so then I would run a #6 - since I don't carry #8- from the panel to the rod.
I am lost. Why is this information relevant?Total load? What size pump and rating? What is the run distance and pump drop in well?
I am lost. Why is this information relevant?
You could save $$$ with less wire size. Distance for conductor size required for V drop and motor load efficiency is not mentioned let alone what voltage is used. Size and type of pump will give reason for not needing to run 3 wire. If sub panel is used then a 3-wire w/g is required. This can help give a better answer for less wire size/cost needed. Using a 6 AWG EGC as mentioned in another reply is conjecture without line and load data.
The question is what size wire to ground rods.
For sub panel one rod is needed, if the casing is metal with proper AWG bonding, no rod needed. Without adequate data, a decent answer is not easy.
For a separate building or structure a grounding electrode system is needed at the separate building or structure. Go to 250 part III and do same thing as you did for the building with the service. If a rod is the only electrode and first one has a resistance of more than 25 ohms you need a second rod. If you can't or don't want to measure the first rod resistance drive the second rod anyway. If some other qualifying electrode other than a water pipe is present then no rod is necessary.
I wouldn't count on a well casing to be metallic beyond the first few feet on anything installed in the past 30 years, maybe even 40 years.
Thank you for making the point about non-ferrous well casings and supply pipes. That is so common in modern rural wells. Other than [250.112(M)] EGC bonding to a utilization equipment BC , would you mention the article for a two electrode requirement that would come into play at a well shed? Tx
250.50 Grounding Electrode System.
All grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present at each building or structure served shall be bonded together to form the grounding electrode system. Where none of these grounding electrodes exist, one or more of the grounding electrodes specified in 250.52(A)(4) through (A)(8) shall be installed and used.
If it is a single circuit just to feed the well pump then no GES is required. (250.32 Exception)
What qualifies something as a "large fastened in place load"?But don't most people want a light in their well house? And then an outlet? I think you could put a light on a 30A branch circuit, but not a receptacle, assuming the fastened-in-place pump was using only 50% of the circuit. But then you show them the screw in light to receptacle adapters while mentioning the common 600W limit on keyless fixtures and the light to recetpacle adapters...
Just about any building should have a panel if its got a large fastened-in-place load IMHO. People usually want a light and receptacle available. Although a multiwire branch circuit fed from handle tied 2A0 and 30A single pole breakers may we a nice way to solve that.