Minneasota Master's

Status
Not open for further replies.

gaylen

Member
Location
Osceola, Wi.
Have a question from the Mn. masters and it was worded What is the minimum feeder demand load of 2 sign/outline lighting outlets. The answers listed were A:1200VA
B:1500VA
C:2400VA
D:3000VA
Please advise Thanks :confused:
 

bphgravity

Senior Member
Location
Florida
Re: Minneasota Master's

The answer is "A". See section 220.14(F) of the 2005 NEC or section 220.3.(B)(6) of the 2002 NEC. Only one sign branch circuit is "required" per section 600.5(A), therefore only one would need to be considered for sizing the service feeder.
 
Status
Not open for further replies.
Top