Yes. I don't see an IR image to go with each pix. :grin:

Also, the equpment seems to have a lot of loose red arrows floating about. You might want to vacuum those out.;)
 
Well, let's see.

Pix #1 is obvious. Someone forgot their crimp tool that day.

Pix #2, hard to tell if it's not a Bellevue washer.

Pix #3, I'm going to say the bolts are not threaded all the way up, so they installed washers so they could tighten the nut down.
 
Well, let's see.





Pix #3, I'm going to say the bolts are not threaded all the way up, so they installed washers so they could tighten the nut down.

That is what it looks like. They could have installed the washers on the bolt head side between the head of the bolt and fitting and installed the the compression fitting tight to the surface or installed proper sized bolts.
 
Pix 2 Steel washer between the conductor termination connector and bus.

Minimal load at time of IR, no thermal image generated by the thermographer.
 
Picture #1
No crimping


Picture #2
Washer between the lug and bus, causing the lug to not make proper connection to the surface of the bus.

Picture #3
The lugs are not making proper surface connection to the bus, which can under load create excessive heat.
I have not seen an installation like this before.

Nice pictures Bryan.

Nice try Pierre. But how about code articles that prohibit this!
 
Number one you need a code reference, for this. Please do not apply for a jonb here.

2 is a listing issue bolt size and hole size, plus the washer.

3 is just commmon sense and may be a listing issue as well.

310.2 (B)
 
Well, let's see.

Pix #1 is obvious. Someone forgot their crimp tool that day.

Pix #2, hard to tell if it's not a Bellevue washer.

Pix #3, I'm going to say the bolts are not threaded all the way up, so they installed washers so they could tighten the nut down.

Belleville is the type of washer. Bellevue is a mental hospital in NY. Please elaborate.
 
Poor Terminations.........

Poor Terminations.........

That kind of stuff..............
NOCRIMP.jpg


is what causes, this kind of stuff........
meter.jpg



No Bueno!
 
Nice try Pierre. But how about code articles that prohibit this!


110.3(B) is the first section I would refer to. The manufacturer's product instructions would be next.

As I have been taught, the surface of the lug is to make contact with the bus, not a washer. The amount of surface area has been computed and designed by the manufacturer, UL and others. That info is found in the product standards and instructions.
 