brantmacga
Señor Member
- Location
- Georgia
- Occupation
- Former Child
I recently installed a VFD for a 20HP submersible pump used for irrigation.
The customer added a backup 20HP pump last week, so we installed a double-throw switch ahead of the VFD to connect both.
The new pump is causing an overload shutdown on the drive.
Existing 20HP pump pulls 55A. The new pump pulls 66A. The box clearly says it’s a 20HP pump, and per the manufacture chart should pull 54.3A.
Could the FLA vary that much, or is it likely mislabeled?
Per the same chart the 25HP has an FLA of 65A. Just by the numbers I think they installed a 25HP.
Sent from my iPhone using Tapatalk