jchristopherslice
Member
- Location
- Greenville, SC, USA
First of all, I am aware that NEC 310.10 prohibits this. However, our client finds them self in a situation where the contractor has installed this contrary to the design. As best we can tell, the design originally (or at other locations) called for 1 set of 4 600 kCM conductors. When changes required 2 sets of 4 500 kCM conductors, apparently the contractor just added one set of 500 kCM, figuring that the other set of 600 kCM would suffice since it was larger than 500 kCM. Our client is looking for justification for temporary code enforcement relief until they can work with the utility to get another set of 500 kCM conductors landed on the utility transformer.
Given that the code says this, why must this be the case? All else being equal, if the relative ampacities of each conductor set created a current divider that didn't exceed the ratings of either feeder, then why shouldn't that be acceptable?
Given that the code says this, why must this be the case? All else being equal, if the relative ampacities of each conductor set created a current divider that didn't exceed the ratings of either feeder, then why shouldn't that be acceptable?