The only issue I would see is with the listing of the fixture itself. If the manufacturer doesnot explicitly state that upsizing is ok for their product there might be a problem with warranty issues. Granted being a govt project, I'm not certain warranties are an issue...
Plus if the picture calls for #8s, I would imagine that would be the issue the inspector is having.
Unless, you resubmitted to accommodate for the #6. My inspector looks at the picture and it better match or he fails the inspection. Rightly so I suppose, but certainly circumstances don't allow for such bureaucratic hoops when time is of the essence.
The inspector may also cite 110.12 for workmanlike installation violations? That might be a stretch, I realize, but it seems to be a go to for some inspectors who can't cite a section immediately or if there is no section to cite.
cheers.