So need some advice here.
THink this is the biggest mistake I've ever made.
Existing commecial building.
Floors we are working on are unoccupied.
Work takes place in a small bathroom that being renovated. There's 50 bathrooms. About 7 on each floor.
THere was a note for 5 of the bathrooms to reconnect new hand dryer to existing curcuit made available after demo.
The problem is the other 45 call for a new 15A circuit in 3/4" conduit back to existing panel. I missed this note.
The panel is about 120' away and it would have to run above existing gypsum board ceilings. THis would have to happen in 45 different areas.
Major hassle. Not even sure EMT could be used because gyp board ceilings.
Curious why they are telling me to use existing circuit for 5 of the bathrooms and not the rest. All the other bathrooms have existing hand dryers being demolished so I could re-use the circuit. But the note says to pull the circuit all the back to the panel and run new. Again, not sure why some are reusing existing and most have to run new.
I really have no defense but I'm hoping the GC( who is very nice) will see he may has to remove or cut holes in the celings for us and pretty sure he didnt figure that and try and push for me to reuse the circuits for the existing hand dryer.
Problem is the engineer who is going to say he bought the new conduit and ask for a credit if we are allowed to reuse the circuit.
Or maybe we reuse the corcuit without telling anyone and see of it goes over?? But then if it doesn't that could be a much bigger issue.
This could be a big issue for me.
BTW can one argue that saying 3/4" conduit could mean FMC and not necessarily EMT.
I'm thinking if I get stuck( which I hope to god I don't) with having to run new circuits I'll say I figured FMC and of they demand EMT hit them with change order.
My have to look for new job...lol
THink this is the biggest mistake I've ever made.
Existing commecial building.
Floors we are working on are unoccupied.
Work takes place in a small bathroom that being renovated. There's 50 bathrooms. About 7 on each floor.
THere was a note for 5 of the bathrooms to reconnect new hand dryer to existing curcuit made available after demo.
The problem is the other 45 call for a new 15A circuit in 3/4" conduit back to existing panel. I missed this note.
The panel is about 120' away and it would have to run above existing gypsum board ceilings. THis would have to happen in 45 different areas.
Major hassle. Not even sure EMT could be used because gyp board ceilings.
Curious why they are telling me to use existing circuit for 5 of the bathrooms and not the rest. All the other bathrooms have existing hand dryers being demolished so I could re-use the circuit. But the note says to pull the circuit all the back to the panel and run new. Again, not sure why some are reusing existing and most have to run new.
I really have no defense but I'm hoping the GC( who is very nice) will see he may has to remove or cut holes in the celings for us and pretty sure he didnt figure that and try and push for me to reuse the circuits for the existing hand dryer.
Problem is the engineer who is going to say he bought the new conduit and ask for a credit if we are allowed to reuse the circuit.
Or maybe we reuse the corcuit without telling anyone and see of it goes over?? But then if it doesn't that could be a much bigger issue.
This could be a big issue for me.
BTW can one argue that saying 3/4" conduit could mean FMC and not necessarily EMT.
I'm thinking if I get stuck( which I hope to god I don't) with having to run new circuits I'll say I figured FMC and of they demand EMT hit them with change order.
My have to look for new job...lol