I have a Mitsubishi Mini-split that has had all the low voltage boards fried twice during a short power outage. No fuses blown on the LV boards, whole house surge protector didn't trip/protect, no breakers tripped. The third heat pump is off line until I can solve this challenge. HVAC tech and commercial electrician have both tapped out with the issue not yet resolved.
The first time this happened the only thing of note was that the single phase voltage was a bit high at 249V. Spec is <253V, which is close/concerning. Utility says it's within spec so not their problem.
After repair a second surge protector (why not) was placed on the circuit to the heat pump. Another power outage happened frying the low voltage boards a second time in less than three weeks. Now and only now after the second event, there is a voltage imbalance between the two hots and ground of about 9V (varies). The imbalance goes away when all loads are shut off and scales roughly with the number of loads turned on and the expected size of the load.
Grounding was vastly improved with the help of a commercial electrician with no impact to the voltage imbalance.
Mitsubishi tech support says the voltage imbalance max spec is only < 3%. This seems to be a weakness that potentially explains the vulnerability of these systems to damage. It's hard to source replacement boards in the U.S., likely because the replacement rate is abnormally high. I was reading the following thread https://forums.mikeholt.com/threads...re-the-same-conductor-with-ac-voltage.102415/ which talks about how the logic signals (low voltage) is sent through the same conductors as the power to the air handler (yes, some models can be ducted).
I don't want to go through this again. The heat pump is currently off line. It's also getting hot out and window units are struggling.
Voltage imbalance is likely an issue with the neutral. But if after a visit from the utility next week results in no willingness to take any corrective action, what do I try next to protect this system? I feel like installing a true isolation transformer, and referencing the secondary to ground to remove the voltage imbalance at the heat pump. Love the heat pump technology overall when it is working. I think the design is not robust enough in my opinion and at $600/board they are making a profit on this design flaw susceptibility to slight over voltage (253V ain't great) and voltage imbalance of <7.2V. That's going to be violated pretty often during a power outage.
It doesn't help that I am experiencing a short power outage roughly once per week since the end of March with only a few exceptions.
What would you do to baby these systems. Buck/Boost transformer or full on isolation transformer?
The first time this happened the only thing of note was that the single phase voltage was a bit high at 249V. Spec is <253V, which is close/concerning. Utility says it's within spec so not their problem.
After repair a second surge protector (why not) was placed on the circuit to the heat pump. Another power outage happened frying the low voltage boards a second time in less than three weeks. Now and only now after the second event, there is a voltage imbalance between the two hots and ground of about 9V (varies). The imbalance goes away when all loads are shut off and scales roughly with the number of loads turned on and the expected size of the load.
Grounding was vastly improved with the help of a commercial electrician with no impact to the voltage imbalance.
Mitsubishi tech support says the voltage imbalance max spec is only < 3%. This seems to be a weakness that potentially explains the vulnerability of these systems to damage. It's hard to source replacement boards in the U.S., likely because the replacement rate is abnormally high. I was reading the following thread https://forums.mikeholt.com/threads...re-the-same-conductor-with-ac-voltage.102415/ which talks about how the logic signals (low voltage) is sent through the same conductors as the power to the air handler (yes, some models can be ducted).
I don't want to go through this again. The heat pump is currently off line. It's also getting hot out and window units are struggling.
Voltage imbalance is likely an issue with the neutral. But if after a visit from the utility next week results in no willingness to take any corrective action, what do I try next to protect this system? I feel like installing a true isolation transformer, and referencing the secondary to ground to remove the voltage imbalance at the heat pump. Love the heat pump technology overall when it is working. I think the design is not robust enough in my opinion and at $600/board they are making a profit on this design flaw susceptibility to slight over voltage (253V ain't great) and voltage imbalance of <7.2V. That's going to be violated pretty often during a power outage.
It doesn't help that I am experiencing a short power outage roughly once per week since the end of March with only a few exceptions.
What would you do to baby these systems. Buck/Boost transformer or full on isolation transformer?