Contractor is using South wire for phase conductor and could not obtain ground wire from the same manufacturer. Is it ok for the ground conductor to be other than South wire?
Contractor is using South wire for phase conductor and could not obtain ground wire from the same manufacturer. Is it ok for the ground conductor to be other than South wire?
Contractor is using South wire for phase conductor and could not obtain ground wire from the same manufacturer. Is it ok for the ground conductor to be other than South wire?
This is a job spec issue. If southwire was submitted and approved and product B was not then an issue could be made. NEC does not prohibit this in the least. Im with Roger. It happens especially when using up leftovers from other jobs.
We typically take exception, as part of the bid process, to specs that call for specific brands of generic items like conduit and wire.Ding Ding! If something goes wrong with these conductors then the contractor that installed them is liable for the damages. If all conductors were submitted and approved by an engineer and something goes wrong, the engineer is liable for the damages. It's a liability issue, nothing else.
Is the op thinking about parallel pulls???
Are you thinking one would need conductors from the same manufacture to be used for a phase?
Shhhh! Don't give the CMP any ideas.
Ooops. Sorry.
Many times for items like wire, conduit, boxes, etc... I will submit a number of manufacturers products, especially if more than one is listed in the specs, the reason being is that when I get ready to make the purchase I will send the package to multiple suppliers for competitive quotes and whoever is low will get the sale.Ding Ding! If something goes wrong with these conductors then the contractor that installed them is liable for the damages. If all conductors were submitted and approved by an engineer and something goes wrong, the engineer is liable for the damages. It's a liability issue, nothing else.
Are you thinking one would need conductors from the same manufacture to be used for a phase?
Welcome to the forum.You might not need the same manufacturer, but be aware regarding speciality wire and how using two different types might void mfr warranty. Example: using lubricant on wires that are manufacturers to be pulled without lubricant - such as SimPull cable, would void their warranty because it can actually cause the wire to resist during the pull. So you wouldn't want to use treated cable, with untreated cable.
Just a thought.
Sent from my iPhone using Tapatalk
Example: using lubricant on wires that are manufacturers to be pulled without lubricant - such as SimPull cable, would void their warranty because it can actually cause the wire to resist during the pull.
Cable Lubrication
Reducing the coefficient of friction is the primary factor in the selection of a lubricant. Compatibility
of the lubricant with cable and conduit is extremely important. The lubricant should not have any
deleterious effects on the conduit or on the physical or electrical properties of the cable insulation, or
jacket materials.
An estimate of the quantity of required lubricant can be determined:
Q = 0.0015
∙L∙D
where: Q = Quantity in gallons
L = The conduit length in feet
D = The inside diameter of the conduit in inches
Southwire Company’s SIMpull® products provide uniform pre-lubrication eliminating the need for messy
lubricants while assuring the same or lower pulling tensions as when adding lubricants during the
installation.