Just curious if anyone mixes PVC conduit with a metal service head when they dont have a PVC one available...allowed by code? How about larger diameter sizes and schedule 80?
 

GerryB

Senior Member
When you twist up your neutral and bend it down so it comes out the notch below the inserts it contacts the metal.

-Hal

I guess it does. I usually use PVC, one job I did in SEU water traveled down the sheathing through the meter and right into the panel. The OP indicated some difficulty getting a PVC weather head. Pretty common item I would think.
 

kwired

Electron manager
Location
NE Nebraska
I'm thinking that a metal weatherhead is not listed for use on a nonmetallic raceway.

That is how I see it. Other than that, they are usually up and out of danger areas and in reality this is sort of not an issue.

I have seen some with a bonding screw/lug and is possible those may be listed for use on nonmetallic raceway, if bonded.
 