mixed voltages in same conduit

Status
Not open for further replies.

pj ski

New member
have a job going on now where hired a sub contractor to run conduits for 25hp 3ph motor, and 24v dc & 24 ac control wires he proceded to put all in same conduit, he says it is not a violation just a common practice no to do ? can you specify ?
thank you
 
Re: mixed voltages in same conduit

It depends. More than likely the control circuit is fed from a class 2 power supply, in which case the contractor is wrong.
 
Re: mixed voltages in same conduit

2nd what peter said, not to mention that, depending on what the dc does, you could drive some control componbets crazy.
 
Re: mixed voltages in same conduit

pj

Read section 725.55

[ December 10, 2005, 04:24 PM: Message edited by: russ ]
 