Mixing 130 VDC & 24VAC

Status
Not open for further replies.

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
in the same raceway.
130vdc is for a door alarm and 24vac is air conditioning controls.
Can I do this or am I mixing class1 and class2?
 
Voltage and insulation type for the conductors are not the only determing factors in regards to conductors from different systems installed in the same raceway/enclosure.

As you mentioned, the source is important as well, such as Class 2.
 
Voltage and insulation type for the conductors are not the only determing factors in regards to conductors from different systems installed in the same raceway/enclosure.

As you mentioned, the source is important as well, such as Class 2.

The source for the door alarm is a 130 volt dc 20 amp breaker in a panel fed by a 130 battery string. The 24 vac source is a control transformer in the air conditioner.
Or do I not understand what you and Raider are asking me?
 
The 24 vac from the air conditioner is probably from a Class 2 power supply and the rules in 725.55 will very likely will prohibit the mixing of those conductors with those of the 130 volt system.
 