Mixing copper and aluminum wires as sub feeders

Merry Christmas
Status
Not open for further replies.
Ilsco makes all sorts of combinations for regular and fine stranded conductors. These are good for #3/0 Al and feature a #1/0 pin.

ACO-3-0.jpg


That appears to be a solid pin and not suitable for use with most electrical equipment designed for conductors larger than 10 AWG, as most of that equipment specifies the terminations are for Class B or C stranded conductors.
 
That appears to be a solid pin and not suitable for use with most electrical equipment designed for conductors larger than 10 AWG, as most of that equipment specifies the terminations are for Class B or C stranded conductors.
So it is star shaped and textures I wonder how this particular pin is listed because it may be able to be used if it's crushed and deformed like a stranded conductor would be.
 
If you could prove that entire feeder is underground in 20 deg C ambient (except for up to 6 ft rise at both ends.) AND that the breaker will limit maximum continues current to 100A. Then #2/0 AL Ampacity at Correction Factor 1.15 will be 132.5. and you could use that wire.

With continues current of 100A the temperature of wire will not exceed 50.2 deg C that would allow to use 60 deg C wire resistance for the calculation and the Voltage drop will stay below 3%.

You may check-out the calculator that produced the screen shot at

 

Attachments

  • VD-AL80.JPG
    VD-AL80.JPG
    200.1 KB · Views: 3
So it is star shaped and textures I wonder how this particular pin is listed because it may be able to be used if it's crushed and deformed like a stranded conductor would be.
Only if you get the breaker listing changed to say it can be used with something other than Class B or C stranded conductors.
 