Re: Mixing neutral and grounding connection
All of my responses to this topic are in consideration of the wiring method being NM cable.
Metal conduit, to a panel, will make two grounding connections. One path will have to be defeated.
There has never been wording in the NEC requiring separation of ground and neutrals in a panel. This is only one method to defeat multiple ground to neutral connections that create common mode current flow.
For years, panels did not have but one factory installed bus. Except in metal conduit wiring methods, one terminal strip should be all that is necessary. This makes the neutral conductor a fault path instead of a smaller conductor.
Engineers reading this thread, please jump in.