Re: Mixing neutral and grounding connection
Bennie
You keep refering your comment back to NM cable. NM cable today has an equipment ground installed with the circuit conductors. Years ago, NM cable did not have an equipment ground and the older panels that were installed did not have an equipment ground either.
Today an equipment grounding conductor is required to be installed to a panel downstream of the first point of disconnect from the serving utility. These downstream panels are not service panels and it will only create more confusion for some by calling them service panels. The delineation for this is not the enclosure, but the disconnect.
In TODAYS installations, everywhere one looks there are metallic paths back to the service disconnect that are the 'effective ground fault current path' for the purpose of opening an overcurrent protective device (fuse, circuit breaker, etc..).
If we were to wire in the fashion you describe, with the REQUIREMENTS that are set forth for us, there would be multiple problems on that system, some of them creating a hazardous situation.
This wiring method we use today has been in place for such an amount of time, that it would become very, very difficult to change to an ungrounded system to rectify some of the problems that a grounded system inherently has.
Including my post, this subject has been beaten to death!!!
Of course this is my opinion
Pierre