housemoney
- Midwest
- Mech Engr
Wiremold multioutlet assembly with 3 separate channels for 2 -120V/20A normal power circuit outlets (each from separate ckt) and 1 -120V/20A UPS power outlet per workstation. Engineer is trying to get us to apply wire markers and cable ties on the UPS circuit citing 200.4(B). That's fine, but I'm trying to understand the hazard with somehow mixing a branch circuit neutral or EGC between the UPS and non-ups systems would necessitate such stringent labeling during construction. The UPS circuits are fed from a single phase 120/240 panel board that's stepped down from a 208V 3 phase output of a static UPS, so it derives it's a SDS that derives it's own neutral point.
If the neutral was accidently swapped between a UPS and normal power outlet, this would simply result in an open circuit, would be noticed and corrected?
If the EGC was accidently swapped between a UPS and normal power outlet, the fault current would take the neutral and the breaker would still trip, just no safety ground on that outlet?
Sorry just thinking out loud as to what the Engineer is thinking here, not trying to challenge him, just understand the deeper technical issue.