Went to lady's mobile home this weekend. Electrician had upgraded the pole service from 100A to 200A with a Main breaker /feed through lugs and 4 slots on pole panel serving as disconnects & OCPDs.
Mobile home had a 100A panel in it witch electrician refed with 100A direct burial cable off the feed through lugs. Cable under trailer was tye wrapped to steel under trailer frame & not in conduit....I guess he is ok with the outside tap rule but no conduit?
Also found that a 100A underground feeder was feeding the AHU in the trailer from the pole panel. (100)A feeder breaker and cable to (2) 60A 2pole breakers in the AHU...also wrong? Didnt look at the wiring feeding the AHU but I am sure it was not in conduit either.
****Guess the main question I have is: can the pole disconnect/service provide (2) feeders to this mobile home? Or must all branch circuits that supply appliances in the mobile home be fed from 1 source within the trailer. The NEC uses terms such as: (A) panel implying only one feeder is allowed.
To top that off NM cable took the last slot in the pole panel...it was used to feed the CU sleeved with the direct burial cable to the underside of the mobile home then to a disconnect on the side of the trailer. No room left for breakers at the pole disconnect .....
Hacks at best
Hacks at best