Curious how the manufacturer came to these values, but I am trying to work out the calculations and verify. Below is for an AC system
Below is for a rooftop unit:
I am curious as I usually use the horsepower of the unit/motor to find the FLC, from there I calculate MCA = 1.25*FLC, and then size the breaker at FLC*2.25. However, none of the mechanical units I am dealing with reflect those calculations.
I am fine using the manufacturer's recommendations, but I usually crosscheck to make sure everything looks right.
Below is for a rooftop unit:
I am curious as I usually use the horsepower of the unit/motor to find the FLC, from there I calculate MCA = 1.25*FLC, and then size the breaker at FLC*2.25. However, none of the mechanical units I am dealing with reflect those calculations.
I am fine using the manufacturer's recommendations, but I usually crosscheck to make sure everything looks right.