How often is this fuse going to blow unless there is physical abuse of the protected conductors or maybe something contacts a terminal?
Is a situation it should never be overloaded unless there is a failure in the supplied equipment. This is also assuming the proper fuse was installed to begin with.
This one was a generator with 4 ATS. It was a complete hack job, they paralleled all the utility sense wires, did not install the transfer relay as required by Generac, had lamp cord feeding some of the ATSs, had an added on battery charge circuit that was connected to the utility lug, so during power loss it wouldn't charge the battery. He'd had a stream of "electricians" out there to try and fix it, and they couldn't figure out why two ATS would transfer over, and two would randomly not.
I re-wired the whole system, set it up as master/slaves, installed the relay, and when I powered it up, one leg of the utility sense wasn't reading, and I found the blown fuse. Apparently it happens a lot when they are wired improperly like that.
As an aside, if you ever find a system wired wrong like that, be careful, because you can shut off the main panel at a unit, and if the utility sense wires are paralleled like that, it'll backfeed the building.