Tip DS
I'm here.
- The Great Meme State
- Electrical Engineer
I am aware a branch device can have its SCCR 'modified' or raised through the use of class listed OCPD (generally a current limiting fuse) up-stream of the device, assuming the let-through current does not exceed the device's withstand current rating.
Here's the heart of my question: Can the same thing be done for the entire branch circuit? For example, let's say a branch circuit has a circuit breaker that protects a contactor, overload relay and motor. Imagine all the components down-stream of the circuit breaker have a SCCR of 100kA, or have been modified to meet 100kA SCCR. NOW, the circuit breaker that's up-stream from all the components only has a SCCR of 14kA. Can I put a 200kA interrupt rated fuse up-stream of the circuit breaker with a let-through current of less that 14kA, and have the entire branch rated at the 100kA of the rest of the modified branch?
In other words, can I have a "modified BRANCH SCCR" in the same way I make a modified component SCCR - with an up-stream fuse (not in the feeder circuit?)