D designer82 Senior Member Location Boston Apr 6, 2025 #1 Would this modular meter center with a main CB count as 1 of the up to 6 allowed service disconnects or would it count as 12? I'm thinking 1 but just want to make sure. Thanks
Would this modular meter center with a main CB count as 1 of the up to 6 allowed service disconnects or would it count as 12? I'm thinking 1 but just want to make sure. Thanks
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Apr 6, 2025 #2 The main would be the service disconnect. The other twelve are not.