480, did we hit it, or are you just giving us more time??
I think sparky isnt sure if there are any violations and he wants us to help him find out.that is why he is not replying yet
but once he sees this post he will reply.
![]()
You must have been a Where's Waldo fan as a kid.I love to play "spot the violations"game.:smile:
As long as there's a 15 or 20 amp breaker before the receptacle, yes.But even if they were, is it illegal to feed a 240v 30a recep and a 120v 15a duplex with a 2-pole breaker?
Unless there was a j-box somewhere, it wouldn't make any difference if it was bare or insulated when 3 wire dryers were code. At one end you take the neutral to the metal of the dryer, on the panel end ( main panel only ) the neutral and EG bus are jumpered.
Not correct, guys.around here it used to be 10-2 copper or 8-2 SE-U.
2 insulated hots and a bare conductor which would technically serve as the neutral and ground.
ok 480 i guess you still want more.![]()
on the 1900 or 2100 box the recpt cover is missing a screw.
the slots on the recpt look to be painted over.
and i would also bet there is no nipple between either the recpt and the disconnect switch or the 1900/2100 box an the disconnect switch.but that just a guess.i don't see the knockouts aligning up
Maybe not benaround. But what I said is absolutely correct. Maybe you are misunderstood like in the other thread. I never said that the ground was being used as the neutral. And it used to be done with 10-2 copper or 8-2 aluminum SE-U before the 4 wire went into effect.Not correct, guys.
The neutral had to be insulated unless it was the bare in a covered service cable. You could use either 10-3 cu NM or 8-2 al SE.
Remember, this exception was allowing the neutral conductor to do the grounding, not the ground conductor being used as a neutral.