Another round of goodies sent me from another Forumer.
![]()
![]()
![]()
![]()
![]()
Nice pics.hows is the transformer being wired.Another round of goodies sent me from another Forumer.
![]()
Looking for some sealtight here.
![]()
And here
![]()
Lug is not pretty and not rated for that # 12 awg wire as well
![]()
In defense of the install, some tray cable doesn't come standard with white.If this is tray cable. Are there two different wires in the main lug. it looks like a fine strand with a course strand.
![]()
Gotta find out whats up here.
Nice pics.hows is the transformer being wired.
looks like an idiot wired that transformer. its obviously a 480v/277v - 120/208v transformer. your supposed to bond XO instead. he used the same size wire for the primary and secondary? might be a waste of money
I noticed there's no conductor connectioned to the Xo at all.
well even if there is no neutral you still need to bond it to the GEC. i doubt that transformer even worked properly. whats the point of having a corner grounded delta anyway in a building? what would they use that for?
looks like an idiot wired that transformer. its obviously a 480v/277v - 120/208v transformer. your supposed to bond XO instead. he used the same size wire for the primary and secondary? might be a waste of money
It will work just fine for the right purpose. I never would have believed it myself either, until I learned about it and actually did an install similar to that.i doubt that transformer even worked properly.
I would look at the photo again before I would call the installer an idiot. For one thing the conductors are not the same size since the 208 volt conductors are paralleled.
![]()
Not that it's a violation, buy why spend the money for double lugs on the high voltage side when there's only one conductor connected to it?
http://i214.photobucket.com/albums/cc172/480sparky/Spot the Violation/STVG15.jpg
![]()
Not that it's a violation, buy why spend the money for double lugs on the high voltage side when there's only one conductor connected to it?
http://i214.photobucket.com/albums/cc172/480sparky/Spot the Violation/STVG15.jpg
i still want to know why H1 is grounded and whats the purpose of that
Because they reverse fed a delta-wye xfmr. Meaning they powered the secondary side to create the delta coming out. And since you can't have an ungrounded system(unless you meet certain requirements) they ground one phase to stabillize voltage.
so its just strictly 3 phase? is H1 a neutral or is it an actual phase conductor?
so its just strictly 3 phase?