conductors of different systems 690.4
conductors of different systems 690.4
mixing different systems in PV is not wise and it is not code. As most of you know DC and AC systems need to be apart in the PV world [300.3(C)1], and the same is for all signal wires i.m.h.o the intent is important here. PV array source circuits may not be mixed [690.4 (B)]. It is not explicit re. signal or low voltage systems, clear on the AC vs. DC.
If you have PV source circuit ever arcing into a signal wire it can make for a "bad day". The array can never be shut down really, and if it ever shorted out with the CAT 5, well it would be a real mess until the sun sets.
725.136 may help as well
tailwinds,
Heilos
conductors of different systems 690.4
mixing different systems in PV is not wise and it is not code. As most of you know DC and AC systems need to be apart in the PV world [300.3(C)1], and the same is for all signal wires i.m.h.o the intent is important here. PV array source circuits may not be mixed [690.4 (B)]. It is not explicit re. signal or low voltage systems, clear on the AC vs. DC.
If you have PV source circuit ever arcing into a signal wire it can make for a "bad day". The array can never be shut down really, and if it ever shorted out with the CAT 5, well it would be a real mess until the sun sets.
725.136 may help as well
tailwinds,
Heilos