N nizak Senior Member Sep 26, 2022 #1 Does the MOP value on an electric strip for supplemental geothermal heat take into account the 125%circuit requirement. Thank you.
Does the MOP value on an electric strip for supplemental geothermal heat take into account the 125%circuit requirement. Thank you.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Sep 27, 2022 #2 Normally, yes. (The heat strip itself should be marked also making it easy to confirm)