So say an Architect gave you an elevation for an outlet at the basin as 8" AFF (Typ to all other outlets) to the side of the basin cabinet. Would you question this? It says, within 3' of the basin, nothing about what direction. Now the real question! If you were, or are an Inspector, would you measure it?
210.52(D) Bathrooms. In dwelling units, at least one wall receptacle outlet shall be installed in bathrooms within 900 mm (3 ft) of the outside edge of each basin. The receptacle outlet shall be located on a wall or partition that is adjacent to the basin or basin countertop.
Section 210.52(D) requires one wall receptacle in each bathroom of a dwelling unit to be installed adjacent (within 36 in.) to the washbasin. This receptacle is required in addition to any receptacle that may be part of any luminaire or medicine cabinet. If there is more than one washbasin, a receptacle outlet is required adjacent to each basin location. If the basins are in close proximity, one receptacle outlet installed between the two basins might satisfy this requirement. ~~~~~~~