Now that the storm has taken all the poco men north, my customer want's to use a genset to temp power. I got an ice machine and a refrigerated shipping container. Ice machine 208 3ph (Min cir 65)(LRA 180). So that's 60 starting kw. The refrigerated shipping container is 480 (25a)and uses a step up tx. 2/1. at 208 we are 50 amps. I can't find any starting amps on the unit. So I use the multiplier for the ice machine 2.8 50*2.8 =140a =40kw to come up with the container. 100kw generator. Am I on the right track????