mbrooke
Batteries Included
- Location
- United States
- Occupation
- Technician
IOW, where the IG remains isolated all the way back to the main or system bonding jumper, where the equipment grounding system originates, the more stable the IG reference is... but who runs the branch circuit IG all the way back to the main.
Only a select few who want a code complaint true IG.
It's usually just to the local panel then a feeder IG back to the main... so any 'noise' contributed by the branch equipment is 'looped' at the local level anyway.
IG amounts to an esoteric system and just how esoteric the designer wants to be.![]()
And it might be enough- or it might not be enough to satisfy power quality requirements. The blunt truth is that most IGs are not real IGs, but rather feel goods or dangerous home brewed concoctions. Retail is a perfect example- techs feel the equipment is protected, but come reality its often just an orange special wired like a regular receptacle.
Manufacturers know that most IGs are a joke, and even where a true IG exists as soon as you interconnect stuff or it touches a typical rack it ends up being grounded through the buildings regular grounding system one way or another. As a result manufacturers are designing equipment that does not give a hoot what type of ground loops or ground voltages are present.