More on Conductor Fill

Status
Not open for further replies.

JohnE

Senior Member
Location
Milford, MA
Occupation
Electrical Contractor, Inspector
One of my guys came in this morning and asked if I would "do the math" for conductor fill or use the tables in annex c. I told him that I'd do the math since I'm used to it and annex C wasn't always there, ( and also the preface to annex C stating that it is not part of this NFPA document), but why do you ask. He said that in a code class the previous evening, they had an example where doing the math for #14 THW resulted in 19.7 conductors being allowed in 1" SCH 80 PVC, but annex C shows only 13. I told him that can't be right. When I double checked, I found it to be true.

I ran 16 examples using #14 and #8 THW and THHN for 1" and 2" sch 80 pvc and emt. I found that every example using thhn correlated with annex C, but every example using THW was drastically different.

For example: #14 THW = .0139 sq. in. from table 5. 1" sch 80 = .275 sq. in @40% fill. So, .275/ .0139 = 19.7, so 19 conductors, no? Annex C (p. 698) shows 13 conductors.

I'd think I were doing something wrong, except his instructor came out with same values.

Maybe we are both doing something wrong.

Any Thoughts?
 
Re: More on Conductor Fill

I checked your example, and agree with your results. I did not check the other THW examples, but I have no doubt you are right.

To quote Ben Franklin:
The fact is singular. You require the reason? I do not know it.
 